Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Please select a country to continue with beta search.
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 01:32 AM . Last Modified: 2024-03-13 05:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:32 AM . Last Modified: 2024-03-13 05:27 AM
Hi All,
This has got to be the most tricky solution I have worked on in the recent past and I think I have done well, expect the last lingering bit. I have a Esxi 5.5 environment which I want to monitor and shutdown using powerchute when the time comes and I have installed the customary vma machine and its on the same subnet as the UPS.
I have installed the powerchute application and I can get to the web url of the application using http://server_ip:3052, I have opened up the firewall ports as well on my vma machine
Now when I login to my powerchute url and try and configure powerchute, I get an error while registering the NMC card as you can see below..
The odd thing is that when I login to my NMC page under UPS -> Powerchute -> Clients ... I can see the ip of my vma machine listed!! Not sure what that means since I get the above registering error message and in the event logs I see
So I have couple of questions
-Alstar
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:32 AM . Last Modified: 2024-03-13 05:27 AM
Hi,
On 12/27/2015 11:23 PM, Ali said:How do I get my NMC card to register with powerchute and what are the implications if I leave it un-registered since I see the IP of my VMA machines in the client list.
99 percent of the time when this happens it is do to mismatched subnet masks. If it is not the subnet mask please review Kbase FA159624 for more troubleshooting steps.
On 12/27/2015 11:23 PM, Ali said:Also how do I configure the network shutdown since I am little un-sure on how to do this.. Like i want the powerchute application to shutdown my esxi host if the UPS battery falls below 30%
PowerChute does not shutdown based on percentage but will based on time on battery or runtime remaining. The User's Guide describes both of these settings starting on page 88.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:32 AM . Last Modified: 2024-03-13 05:27 AM
Hi,
On 12/27/2015 11:23 PM, Ali said:How do I get my NMC card to register with powerchute and what are the implications if I leave it un-registered since I see the IP of my VMA machines in the client list.
99 percent of the time when this happens it is do to mismatched subnet masks. If it is not the subnet mask please review Kbase FA159624 for more troubleshooting steps.
On 12/27/2015 11:23 PM, Ali said:Also how do I configure the network shutdown since I am little un-sure on how to do this.. Like i want the powerchute application to shutdown my esxi host if the UPS battery falls below 30%
PowerChute does not shutdown based on percentage but will based on time on battery or runtime remaining. The User's Guide describes both of these settings starting on page 88.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.