Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84713members
354108posts

Clearance requirements for a Symmetra PX 20kW 208V Model #

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

AK_EE
Cadet
0 Likes
1
247

Clearance requirements for a Symmetra PX 20kW 208V Model #

What are the rear and side clearance requirements for the Symmetra PX 20kW 208V unit? Model # SY20K40F.

 

None of the manuals available online appear to have this information. I plan on bottom entry, so I don't need rear access for cable installation.

Tags (3)
1 Reply 1
al_buffington
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
238

https://download.schneider-electric.com/files?p_File_Name=ASTE-6Z4KMR_R1_EN.pdf&p_Doc_ReRe: Clearance requirements for a Symmetra PX 20kW 208V Model #

Hi,

 

Front and rear clearance should be 36". Side clearance is not required. You can find this in the receiving and unpacking guide (link below). Hope this helps. 

 

https://download.schneider-electric.com/files?p_File_Name=ASTE-6Z4KMR_R1_EN.pdf&p_Doc_Ref=SPD_ASTE-6...