Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cannot talk to the UPS using AP9630

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Cannot talk to the UPS using AP9603
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
sdas_apc
sdas_apc
Contributor

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:39 AM

0 Likes
2
3471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:39 AM

Cannot talk to the UPS using AP9630

Hi there!

My first APC in a very long time also fist post in this forum, so my apology in advance, if this has been answered.

I recently bought a SMT1000RMI2UC and AP9630 to go in it. They both seem to be working file as their own but I cannot talk to the UPS from the client using apcupsd. I tried with pfSense and also a from a vanilla Ubuntu (18.04) but all resulted in the same thing.

So, this is my apcupsd.conf:

QfkKFOAPHivp0pzkStALPg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngQfkKFOAPHivp0pzkStALPg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

The service seems start okay but within a min or so, I get  the message saying communication has been lost:

6dnOVN45UmoC8ibCJycj0g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png6dnOVN45UmoC8ibCJycj0g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

and the STATUS is always COMMLOST:

eRzu54a8nqpmt8wAJB2lMA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngeRzu54a8nqpmt8wAJB2lMA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Thing to note that I'm using PCNET over Ethernet (as opposed to directly USB-attached). All the firmware are updated to it's latest:

4qAvgvzlheBR3A%2BgUfRCow%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png4qAvgvzlheBR3A%2BgUfRCow%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png 

Does anyone know what am I doing wrong? Any help will be greatly appreciated. Doesn't look like the card or UPS is faulty, right?

-S 

 

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9630
  • communication
  • firmware
  • nmc2
  • smt1000i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sdas_apc
sdas_apc
Contributor

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

0 Likes
0
3471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

Hi Gavan, thanks for your reply!

I figured out last night why it was not working. I think, how it's supposed to work not really documented clearly, at least I didn't find out....... but scattered around in this forum discussions and the some of the docs. First of all, for the PCNET type, it uses pass/auth phrase instead of password and that needs to defined in the NMC web-gui, which is placed in rather odd-place: under Configuration > Shutdown

bC00JCaNYyrx2OKWJniC1w%3D%3D.pngbC00JCaNYyrx2OKWJniC1w%3D%3D.png

re. https://www.se.com/uk/en/faqs/FA159659/

That user (e.g. netman, which I setup as a network-only user) must be created first. PCNS uses both the password & pass-phrase for that user and  APCUPSD uses only the pass-phrase. After that both started working. 

-S

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

0 Likes
0
3471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

Hi Santanu,

APCUPSD is a third party software so I can't help you with that, but what I would recommend is that you look at Powerchute Network Edition. PCNS supports Ubuntu and may other types of Linux, you can download it from the link below:

https://download.schneider-electric.com/files?p_enDocType=Software+-+Released&p_Doc_Ref=1DTR_PCNS_43...

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

sdas_apc
sdas_apc
Contributor

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

0 Likes
0
3472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:26 AM . Last Modified: ‎2024-03-15 05:38 AM

Hi Gavan, thanks for your reply!

I figured out last night why it was not working. I think, how it's supposed to work not really documented clearly, at least I didn't find out....... but scattered around in this forum discussions and the some of the docs. First of all, for the PCNET type, it uses pass/auth phrase instead of password and that needs to defined in the NMC web-gui, which is placed in rather odd-place: under Configuration > Shutdown

bC00JCaNYyrx2OKWJniC1w%3D%3D.pngbC00JCaNYyrx2OKWJniC1w%3D%3D.png

re. https://www.se.com/uk/en/faqs/FA159659/

That user (e.g. netman, which I setup as a network-only user) must be created first. PCNS uses both the password & pass-phrase for that user and  APCUPSD uses only the pass-phrase. After that both started working. 

-S

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore