Posted: 2025-07-03 03:26 AM
Hello,
I have a SRT 10kW that gives the error "Battery temperature sensor error for battery pack 1" .
What can be the issue?
The UPS has firmware: ID:1014 UPS:04.7
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-03 08:22 AM
Provide the following logs from the system: Event, Data, UPS. Upload a screen capture of the About tab for the NMC & UPS.
Complete this procedure as outlined in this APC Video FAQ relating to the SRT and report back the results.
Brain Dead: https://www.se.com/ph/en/faqs/FA156611/
If the problem remains after the brain dead procedure then remove the RBC and power cycle the system and report back if the active fault is gone and replaced (only) with a battery disconnected / missing fault.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-03 08:22 AM
Provide the following logs from the system: Event, Data, UPS. Upload a screen capture of the About tab for the NMC & UPS.
Complete this procedure as outlined in this APC Video FAQ relating to the SRT and report back the results.
Brain Dead: https://www.se.com/ph/en/faqs/FA156611/
If the problem remains after the brain dead procedure then remove the RBC and power cycle the system and report back if the active fault is gone and replaced (only) with a battery disconnected / missing fault.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-07 06:43 AM
Well?!?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of