Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Battery needs replacing - causing coldstarts on all equipment.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery needs replacing - causing coldstarts on all equipment.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5029
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
10
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

Battery needs replacing - causing coldstarts on all equipment.

This was originally posted on APC forums on 7/23/2009


Have a SmartUPS 3000 RM with 4 servers attached that is in need of battery replacement. The excerpt from the log file below indicates as much.

Problem is that the UPS is killing power to all the servers on an almost daily basis (usually just before working hours.. you can see all the "coldstarts" in the log..)

I understand that the battery needs to be replaced, but why would this cause the UPS to kill power to all my systems?
There have been no power events, so why doesn't the UPS just continue to provide pass-through power from the wall.

It would appear that something is wrong or misconfigured on the UPS (but I can't find it) or there is a poor design that would sacrifice the stability of all servers just when a battery is low.

Any help would be appreciated.

Thanks.

Log Excerpt Attached

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/24/2009


The reboots happen during off hours, so there is no one to see the unit's lights or hear beeps.

In addition, the servers come up with the unexpected shutdown message, which most likely means that they had power forcibly removed and were not asked to shut down via a network message.

- And another thing regarding the events log... it seems that you are saying that the log is only showing events from the NMC and not the UPS itself (or vice-versa)? Nowhere in the log is there any indication of any type of power event other than the battery needs replacing and the coldstarts (which previous poster said was an issue with the NMC). How is one to differentiate what is an event from the NMC vs. a UPS event? It seems that there should be a more detailed log other than the event.log, but that seems to be the only one that exists.

thanks

Message was edited by: BH

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This reply was originally posted by Jonathan on APC forums on 7/23/2009


Hi Ben, can you also include the data logs from the network management card where this UPS is listening?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/23/2009


The K-base ID: 2572 says that a Coldstart event indicates that the NMC (Network Management Card) has just been powered and has completed startup.
Click on the below link for more information.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2572

If possible, could you please post the data logs which were recorded when the cold start events recorded?

Reply

Link copied. Please paste this link to share this article on your social media post.

BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/23/2009


I'm not sure what the other logs requested are.

The log I attached is the log that shows when I connect to the Management Card's web interface and go to the Event Log.

I see nothing under there that indicates a "Data Log"

The UPS mgmt. card is at 10.10.2.5 which is where I go for web access. I can also open up the APC software on each server that is configured for network shutdown.

Can you please elaborate on what data you need?

thanks

p.s. That link that describes the NMC behavior...not sure I understand it because it states that if a device powering the NMC loses power.... but isn't the NMC powered by the UPS itself? By that I mean the NMC is installed in the UPS and derives its power from the same source, namely the wall outlet.

So I'm not sure if you are trying to indicate that we are losing power from the wall and then the servers are getting powered off because of a bad battery. If that were the case, I would expect to see a UPS event that shows on battery power if even briefly. But, perhaps I am overlooking a log file as mentioned above.

Message was edited by: BH

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This reply was originally posted by Jonathan on APC forums on 7/23/2009


Ben,

Here is the guide that can help you retrieve the data and event logs as well as the config.ini files on your network management card.
[How can I download Event logs and Data logs and Config.ini from the Network Management card?|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9321&p_created=1213880132&p...]

Reply

Link copied. Please paste this link to share this article on your social media post.

BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/23/2009


Followed those instructions.

Only one of those files that exists is the event.txt, which is where I provided the previous excerp from.

I have attached it in its entirety.

Thanks

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/23/2009


More info...don't know if it is relevant.

This is an AP9606 NMC. When I took over this environment, there were some issues with installing the network software that required a firmware upgrade. I couldn't find any info from APC on how to get and/or perform an upgrade. Googling led me to results which allowed me to perform the firmware upgrade. I'm not sure if this was the original site I found the info, but here are the release notes and firmware update files I used:

http://www.moscoso.org/pub/hardware/apc/hardware/webcard/firmware/sumx/v326/

I don't know if there is another newer update, as stated I couldn't find anything from APC on updating the AP9606

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This reply was originally posted by Jonathan on APC forums on 7/23/2009


Thanks for that information Ben. We're actually helping another customer upload the updated firmware on an AP9606 on another thread -- [http://forums.apc.com/spaces/6/racks-rack-accessories-cooling/forums/general/5818/2-inrow-sc-unusual...] you might want to check it as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/23/2009


Well, as stated I had already upgraded to a pretty new version. My telnet session reports the following:

Web/SNMP Management Card AOS v3.2.5
Smart-UPS & Matrix-UPS APP v3.2.6

I will review the other thread you posted, but unless there is a known issue with the problem I describe, then the firmware probably isn't the cause.

What else can we look to, (or what would you have me try) to determine why the UPS is rebooting all the servers on an almost daily basis. Again, I'm sure replacing the battery will prevent this (and we are ordering one now), but even with an old battery, the UPS shouldn't reboot the servers.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This reply was originally posted by Jonathan on APC forums on 7/23/2009


Ben,

During those times wherein the servers restarted, did the UPS beeped or any LED that lit up? What was the behavior of that unit? Have you tried disconnecting the card from the network? It could be that the card is sending shutdown signal over the network.

Reply

Link copied. Please paste this link to share this article on your social media post.

BH_apc
Ensign BH_apc
Ensign

Posted: ‎2021-06-28 10:35 PM

0 Likes
0
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM

This was originally posted on APC forums on 7/24/2009


The reboots happen during off hours, so there is no one to see the unit's lights or hear beeps.

In addition, the servers come up with the unexpected shutdown message, which most likely means that they had power forcibly removed and were not asked to shut down via a network message.

- And another thing regarding the events log... it seems that you are saying that the log is only showing events from the NMC and not the UPS itself (or vice-versa)? Nowhere in the log is there any indication of any type of power event other than the battery needs replacing and the coldstarts (which previous poster said was an issue with the NMC). How is one to differentiate what is an event from the NMC vs. a UPS event? It seems that there should be a more detailed log other than the event.log, but that seems to be the only one that exists.

thanks

Message was edited by: BH

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc