Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS 850 start-up - intermittently fails with continuous whistling noise.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Back-UPS 850 start-up - intermittently fails with continuous whistling noise.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
pete99
pete99
Explorer

Posted: ‎2025-02-21 02:17 AM

0 Likes
6
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 02:17 AM

Back-UPS 850 start-up - intermittently fails with continuous whistling noise.

I have a APC Back-UPS 850 uninterruptible power supply. Sometimes when I switch it on it goes through the normal testing sequence but then all the leds go out and it makes a continuous whistling sound. If I switch it off and repeat, it normally starts up correctly.

 

PowerChute self-test passes.  The last battery replacement date, which must be when I bought the device, is September 2022.  The average load on the battery is consistently below 150 watts and the estimated battery time is over 20 minutes, which is pretty much what I remember it being when the device was new.

 

It's irritating but I can work round it.  Just wondering if there is an explanation or solution?

 

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Teken
Champion

Posted: ‎2025-02-21 07:40 AM

0 Likes
5
1949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 07:40 AM

Connect the unit to a computer running APC Power Chute Software. The system should indicate any active faults / error codes provide that information here for review.

 

You also have the ability to provide the data, event, ups logs. Upload them here for review so better insight can be given.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

pete99
pete99
Explorer

Posted: ‎2025-02-22 06:18 AM

In response to Teken
0 Likes
4
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-22 06:18 AM

Thanks for this.  I would say that my original post did say Iwas using APC Power Chute and that there is no indication anywhere of any failure.  The only "ups logs" I can find in the software are the PowerChute Technical Data, which I have attached and which reports "Result of last manual self-test: Passed".

 

To clarify my initial post, I press the power button on the UPS, it goes through the self test routine, then all the leds go out and it makes what I can best describe as a whistling sound from the internal speaker of the ups.

 

The only non-informational Windows Event Viewer events for APC Data Service or APC UPS Service are a couple of older "PowerChute not communicating with the battery backup." errors.

 

However, now I think about it, this is all irrelevant as the issue I'm reporting is when I'm pushing the power button of the UPS on in the first place - i.e. before the computer is booted.

Attachments
PowerChute Technical Data.txt
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-02-24 02:21 AM

In response to pete99
0 Likes
3
1884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-24 02:21 AM

You can install SPC PCSS software for better insight for event, data, ups logs. In the interim remove AC Mains and report back how long the system operates for on battery power.

 

Report back what the system indicates the battery voltage is prior and after the lights out test.

 

Once the UPS shuts down disconnect the battery and measure the voltage. Report back if it matches what Power Chute indicated.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

pete99
pete99
Explorer

Posted: ‎2025-02-27 06:32 AM

In response to Teken
0 Likes
2
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 06:32 AM

SPC PCSS software does not work for me.  The browser says the (self-signed) certificate is invalid.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-02-27 08:27 AM

In response to pete99
0 Likes
1
1852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 08:27 AM

You just need to ignore the error message and say yes to proceed. 

Reply

Link copied. Please paste this link to share this article on your social media post.

pete99
pete99
Explorer

Posted: ‎2025-02-28 01:57 AM

In response to Teken
0 Likes
0
1825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 01:57 AM

Thank you, but not in latest versions of Edge and Firefox on Windows 11.  Ridiculous that a piece of software would have this obvious gotcha.  (Possibly the issue with PCSS is due to time zones and the self-certification : I am in UK, it was morning and possibly it relies on US time zones?)

 

In any case, I posted the question thinking my issue would be something others had experienced and solved.  It seems that's not the case.  The issue only happens fairly occasionally so, rather than trying for a second time to get into PCSS and more determinedly work round the https issue (to collect data, not solve my issue), I think at this stage I'll just live with the issue.

 

Thanks to everyone for their responses.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore