Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BR1000MS randomly shuts off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: BR1000MS randomly shuts off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
healier
healier
Explorer

Posted: ‎2026-09-28 07:49 PM

0 Likes
1
45
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-28 07:49 PM

BR1000MS randomly shuts off

I've been having this issue since the early days of owning this unit, i bought it in July 2023 and ever since it randomly powers off just like if you hold the power button to turn it off causing everything that is connected to it to shut down too. However i noticed that this only happens once the voltage rises to 132v and the AVR kicks on, powering it back on shows no problem, it self tests as usual and unplugging it from the wall switches it to battery as normal. No errors on the screen, unfortunately this problem evolved where its shuts off like it did before but now the ups freezes and remains unresponsive until you disconnect and reconnect the battery, in this state there is no power output from the ups, but the power led button remains lit, unplugging it does nothing too, also for this kind of failure the voltage doesn't matter anymore, it can be normal when before there wasn't any issues, now there is. Battery is 3 years old tho, however that doesn't explain why this problem is present since i bought it.

 

Model: Back UPS Pro BR1000MS

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Teken
Champion

Posted: ‎2026-09-29 01:10 AM

0 Likes
0
40
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-29 01:10 AM

Provide the logs from APC Power Chute (PCSS) following this FAQ:

 

https://www.se.com/us/en/faqs/FA159672/

 

If PCSS isn’t installed you may use the main product link to download a copy:

 

https://www.se.com/ca/en/product/BR1000MS/apc-backups-pro-1000va-600w-tower-120v-10x-nema-515r-outle...

 

Once done leave the UPS connected to the computer running PCSS for a minimum of three days (72) hours. Insure the software is defined and programmed to (NOT) shutdown the target computer system.

 

Screen capture the event & data tabs while performing the following action items:

 

Disconnect AC Mains from the wall outlet and verify PCSS reflects a loss of AC Power. Time how long the unit continues to operate for with the same loads attached.

 

Once the unit shuts down provide a screen capture of the event & data tabs. Download (export) the PCSS logs again and upload both logs for review.

 

Keep in mind the computer running PCSS should be powered by a separate outlet and (NOT) the UPS.

 

Once the UPS turns off reapply AC Mains Power and let the unit fully charge the RBC. Screen capture the event & data tabs and redownload the PCSS Logs for review.

 

Questions Ask . . . 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore