Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Available runtime has been exceeded

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Available runtime has been exceeded
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
TerrierJim
TerrierJim
Explorer

Posted: ‎2026-01-16 06:23 AM

0 Likes
1
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-16 06:23 AM

Available runtime has been exceeded

Hi

 

I have a Smart-UPS SRT 6000 with a Dell PowerEdge R760 connected that runs Windows Server 2022. It's a Hyper-V host with 5 VMs. The host runs PowerChute Network Shutdown 5.2.0.

 

A few days ago I was installing Windows Updates on the host and VMs, when a notification from PowerChute appeared that the server will be shut down. This was unexpected since the UPS was not running on battery at the time and had 4 hours of runtime remaining. There were no power cuts and the UPS was running on mains power the whole time.

 

The PCNS logs show 'UPS critical event: Runtime Exceeded'. and 'UPS critical event Runtime Exceeded triggered a shutdown'. prior to the server being shutdown automatically by PCNS.

 

I understand this is normal if the amount of time it will take for the server and VMs to shut down exceeds the runtime remaining on the battery, but this wasn't the case. I had several hours of runtime remaining and there's only one physical server plus 5 VMs to shut down.

 

I booted the server several times and the same events were triggered, and the server was shutdown automatically after a few minutes each time.

 

I have disabled the shutdown option in PCNS on the Runtime exceeded event for now, until this can be resolved.

 

I have noticed that every time PCNS boots up it logs a 'Available runtime exceeded' event. It looks like it has always done this since the UPS was purchased, but the actual shutdowns only started occurring a few days ago during the Windows Updates maintenance window.

 

Any advice please?

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
BillP
BillP Leader
Leader

Posted: ‎2026-01-21 06:31 AM

0 Likes
0
315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-21 06:31 AM

@TerrierJim 

 

Available runtime has been exceeded in most cases has little to do with the battery runtime. To prevent the shutdown you must disable shutdown for the event "Available runtime exceeded." That can be done through the PowerChute web UI or the pcnsconfig.ini file.

Disable runtime exceeded.png

To change the setting via the pcnsconfig.ini file stop the PowerChute service (on Windows open a command prom

event_RunTimeExceeded_enableShutdown = true, to event_RunTimeExceeded_enableShutdown = false

 

Condition that cause the issue for Microsoft Hyper-V configurations. 
For conditions 1 and 62below, the "total shutdown time" includes the following durations:

  • VM migration duration - Hyper-V only
  • VM shutdown and startup duration- Hyper-V only
  • Host Maintenance duration - SCVMM only
  • Shutdown command file duration
  • SSH action duration
  • Built-in duration of 2 minutes (this consists of a 10 second OS shutdown duration and a 60 second OS shutdown duration; rounded up)

The event occurs with either of the following conditions:

Condition 1 for Hyper-V:
When the total shutdown time required by PowerChute is greater than the Low Battery Duration minus two minutes configured for the UPS. In the event of a low battery condition, PowerChute will not have enough time to complete the shutdown sequence before the UPS powers off. For example, if the total shutdown time required is 3 minutes and Low Battery Duration is 4 minutes, the Available Runtime has been Exceeded event will be triggered.

Condition 2 for Hyper-V:
When the shutdown duration configured for the UPS On Battery event plus the total shutdown time required by PowerChute is greater than the Runtime Remaining on the UPS minus two minutes. This condition can be caused by having too great a load on the UPS when the battery is fully charged.

 

See Schneider Electric FAQ FA241713 for more information on the error "available runtime has been exceeded". for all operating systems.

Also please review Schneider Electric FAQ FA405707 "What is the Low Battery Duration setting used for?"

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore