Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APDU10150ME Cascade Setup – Correct QNA Host/Guest Configuration and Ethernet Cabling

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APDU10150ME Cascade Setup – Correct QNA Host/Guest Configuration and Ethernet Cabling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Netarch
Netarch
Explorer

Posted: ‎2026-10-22 01:32 AM

0 Likes
0
92
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-22 01:32 AM

APDU10150ME Cascade Setup – Correct QNA Host/Guest Configuration and Ethernet Cabling

 

Hi,

 

I am trying to configure two APC/Schneider NetShelter Rack PDU Advanced APDU10150ME units in Cascade mode so that both PDUs can be centrally monitored and managed through a single management IP address.

 

Both PDUs are:

 

Model: APDU10150ME
Firmware: 2.0.8.2
Hardware Version: 2.0
Quantity: 2

The intended topology is:

Management Network

PDU1 - Host
X.X.X.X
|
Cascade Link
|
PDU2 - Guest

 

The objective is for PDU1 to operate as the Host, with PDU2 operating as the Guest and ultimately managed through PDU1 rather than requiring its own permanent management IP address.

 

Schneider documentation states that APDU10-series Rack PDUs support Cascade mode, allowing up to 32 Rack PDUs to be connected using one IP address, with information and data from Guest PDUs gathered by the Host PDU.

 

I understand this is different from Redundant Network Access (RNA), which is the default mode.

 

CURRENT CONFIGURATION

Originally both PDUs were operating in RNA mode.

Using the CLI, I found the following command:

dev cascade [rna/qna] [init] [create]

I changed both PDUs from RNA to QNA.

The Configuration Log confirms:

DaisyMode configuration is changed to QNA from RNA

Both PDUs now report:

SUCCESS
Cascading unit number : 1
Cascading address list: 0
Cascade Mode : QNA

COMMANDS TESTED

On PDU1 I have run:

dev cascade qna create

The PDU responded:

SUCCESS
Reboot required for change to take effect
System Reboot now, Are you sure?(Y/N):Y

After the management controller rebooted, I checked:

dev cascade

and received:

SUCCESS
Cascading unit number : 1
Cascading address list: 0
Cascade Mode : QNA

I have also run on PDU1:

dev cascade qna init

This was also successful and requested the management controller to reboot.

On PDU2 I have run:

dev cascade qna init

This was also accepted successfully and requested a reboot.

After all the changes and reboots, BOTH PDUs still individually report:

SUCCESS
Cascading unit number : 1
Cascading address list: 0
Cascade Mode : QNA

 

Therefore neither unit appears to have become a Guest, and PDU1 does not display another member within its Cascading address list.

 

PHYSICAL CONNECTION TESTED

PDU1 currently has its normal management connection and address:

PDU1 Management IP: X.X.X.X

PDU2 currently has an independent management address for configuration and testing:

PDU2 Management IP: X.X.X.X

 

I have physically connected:

PDU1 ETH1
|
| Standard Ethernet patch lead
|
PDU2 ETH1

 

Both units have been configured for QNA, but PDU2 is still not discovered or adopted by PDU1.

 

QUESTIONS

Could anyone familiar with APDU10/APDU10150ME cascading please confirm the exact supported procedure?

1. What is the correct physical cabling arrangement between two APDU10150ME PDUs?

For example:

PDU1 ETH1 -> PDU2 ETH1

or:

PDU1 ETH1 -> PDU2 ETH0

or is another physical arrangement required?

2. What exactly does QNA represent on the APDU10150ME?

The PDU Configuration Log specifically reports:

DaisyMode configuration is changed to QNA from RNA

3. What exactly do the following CLI commands do?

dev cascade qna init

dev cascade qna create

4. Which command should be executed on the Host PDU?

5. Which command should be executed on the Guest PDU?

6. What is the correct sequence for configuring the cascade?

For example, should the sequence be:

- Configure Host
- Configure Guest
- Reboot management controllers
- Connect cascade cable
- Create the cascade

or should the physical cascade connection already be present before running the CLI commands?

7. Does the Guest PDU initially require its own management IP/network connection while joining the cascade?

8. Once successfully joined, should the Guest PDU's independent management connection/IP be removed so that administration and monitoring occur entirely through the Host?

9. Both PDUs currently report:

Cascading unit number : 1

Should the Guest automatically receive a different Cascading unit number once successfully joined?

10. Both currently report:

Cascading address list: 0

What should the Cascading address list show for a successful two-PDU cascade?

11. Are there specific requirements for:

- Ethernet port selection
- Cable type
- Maximum cascade cable length
- Firmware versions
- Identical PDU SKUs
- Host/Guest configuration order
- Initial Guest addressing

12. Is there an additional Host/Guest adoption, discovery or pairing operation required after changing DaisyMode from RNA to QNA?

13. Is QNA the correct Cascade operating mode for these APDU10150ME units, or is there another configuration required in addition to QNA?

 

I am specifically looking for the procedure applicable to the APDU10/APDU10150ME generation.

 

I am aware that older APC AP8xxx Network Port Sharing uses a different IN/OUT port and terminator arrangement, so I do not want to apply the AP8xxx procedure to the APDU10150ME unless Schneider confirms it is applicable.

 

If anyone has a working APDU10150ME cascade, it would be extremely helpful if you could provide:

- Exact physical port-to-port cabling
- Host CLI commands
- Guest CLI commands
- Exact init/create sequence
- Required reboot order
- Expected dev cascade output after successful joining
- Screenshots of a working cascade
- Any relevant Schneider documentation or configuration examples

 

Any assistance from someone who has successfully configured an APDU10/APDU10150ME Host/Guest cascade would be greatly appreciated.

 

Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore