Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

APC UPS with Network Shutdown script needed to shut the SAP ECC 6 server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS with Network Shutdown script needed to shut the SAP ECC 6 server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

0 Likes
1
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

APC UPS with Network Shutdown script needed to shut the SAP ECC 6 server

Hello All,

I am using SmartUPS SUA1500i with network management card 9617 connected to the network. I have installed the PCNS Network Shutdown software on my desktop running Windows 2008 Server 64bit. The SAP ECC 6.0 EHP5 w/ Orcale 10.x g server is installed and running in the Windows server environment.

I have the following queries regarding my current setup.

1. In case of a power outage and battery capacity run out , I need a script to safely shutdown the SAP server first and then do the graceful shutdown of the Windows 2008 Server, instead of directly turning off the operating system. Any abnormal shutdown of SAP server almost always results in a massive corruption at the database level and requries a huge effort to restore the database to a previous state, that too if the archive logs are intact and a recent backup is available.

I have read on this site about the availability and validity of my scenario πŸ™‚ however it does not mention the script.

[http://www.bomara.com/APC/pcshutdown-sap.htm]

I would be grateful if someone can share any example script so I can get a clue to get the script working in "FlexiEvents" in PowerChute Plus.

2. The second scenario is almost the same except that the SAP ECC 6.0 server is now running inside a (VMWare) virtual machine (running a guest Windows 2008 64bit server on a host Windows 2008 64bit server) executed via VMPLayer/VMWorkstation on the same Windows 2008 64bit server. In case any script is available, how to direct the script to shut down the SAP ECC 6.0 server running inside the Virtual Machine, then shutdown the virtual machine and then shutdown the host Windows 2008 server.

I hope I am able to explain my scenario, for any further queries you are free to reply.

Thanks for the answers.

Cheers.

Message was edited by: AquaFire

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

0 Likes
0
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

Hello All,

I am using SmartUPS SUA1500i with network management card 9617 connected to the network. I have installed the PCNS Network Shutdown software on my desktop running Windows 2008 Server 64bit. The SAP ECC 6.0 EHP5 w/ Orcale 10.x g server is installed and running in the Windows server environment.

I have the following queries regarding my current setup.

1. In case of a power outage and battery capacity run out , I need a script to safely shutdown the SAP server first and then do the graceful shutdown of the Windows 2008 Server, instead of directly turning off the operating system. Any abnormal shutdown of SAP server almost always results in a massive corruption at the database level and requries a huge effort to restore the database to a previous state, that too if the archive logs are intact and a recent backup is available.

I have read on this site about the availability and validity of my scenario πŸ™‚ however it does not mention the script.

[http://www.bomara.com/APC/pcshutdown-sap.htm]

I would be grateful if someone can share any example script so I can get a clue to get the script working in "FlexiEvents" in PowerChute Plus.

2. The second scenario is almost the same except that the SAP ECC 6.0 server is now running inside a (VMWare) virtual machine (running a guest Windows 2008 64bit server on a host Windows 2008 64bit server) executed via VMPLayer/VMWorkstation on the same Windows 2008 64bit server. In case any script is available, how to direct the script to shut down the SAP ECC 6.0 server running inside the Virtual Machine, then shutdown the virtual machine and then shutdown the host Windows 2008 server.

I hope I am able to explain my scenario, for any further queries you are free to reply.

Thanks for the answers.

Cheers.

Message was edited by: AquaFire

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

0 Likes
0
828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 01:23 AM . Last Modified: β€Ž2024-03-06 01:48 AM

Hello All,

I am using SmartUPS SUA1500i with network management card 9617 connected to the network. I have installed the PCNS Network Shutdown software on my desktop running Windows 2008 Server 64bit. The SAP ECC 6.0 EHP5 w/ Orcale 10.x g server is installed and running in the Windows server environment.

I have the following queries regarding my current setup.

1. In case of a power outage and battery capacity run out , I need a script to safely shutdown the SAP server first and then do the graceful shutdown of the Windows 2008 Server, instead of directly turning off the operating system. Any abnormal shutdown of SAP server almost always results in a massive corruption at the database level and requries a huge effort to restore the database to a previous state, that too if the archive logs are intact and a recent backup is available.

I have read on this site about the availability and validity of my scenario πŸ™‚ however it does not mention the script.

[http://www.bomara.com/APC/pcshutdown-sap.htm]

I would be grateful if someone can share any example script so I can get a clue to get the script working in "FlexiEvents" in PowerChute Plus.

2. The second scenario is almost the same except that the SAP ECC 6.0 server is now running inside a (VMWare) virtual machine (running a guest Windows 2008 64bit server on a host Windows 2008 64bit server) executed via VMPLayer/VMWorkstation on the same Windows 2008 64bit server. In case any script is available, how to direct the script to shut down the SAP ECC 6.0 server running inside the Virtual Machine, then shutdown the virtual machine and then shutdown the host Windows 2008 server.

I hope I am able to explain my scenario, for any further queries you are free to reply.

Thanks for the answers.

Cheers.

Message was edited by: AquaFire

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of