Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

APC Smart-UPS 700, PowerSchute 8.0.1, W2000Server - not running

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: APC Smart-UPS 700, PowerSchute 8.0.1, W2000Server - not running
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
kukulac_apc
Crewman kukulac_apc
Crewman

Posted: ‎2021-06-30 08:39 AM

0 Likes
2
544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:39 AM

APC Smart-UPS 700, PowerSchute 8.0.1, W2000Server - not running

This was originally posted on APC forums on 7/11/2009


Hello,

i have APC Smart-UPS 700 connected to server (W2000 Server) via serial port. I have installed APC PowerChute Business Edition 8.0.1 and it is not running - i can not log in, i wonder why i have to login because i want to set up only this local APC.

During installation APC Smart-UPS 700 was found on COM1. Before installation i have installed the newest version of Java JRE.

Application says that it could not connect to APC PowerChute Business Edition Server. I have also noticed that pbeserver service is not running. When i want to start it manually it says: StartServiceControlDispatcher failed!

Does anyone know what is wrong? Or does exist some other application to manage my APC?

Thank you for your advice, Franta.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 700
  • apc
  • business
  • edition
  • installation
  • manage
  • PowerChute
  • serial
  • server
  • smart-ups
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 08:39 AM

0 Likes
0
542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:39 AM

This was originally posted on APC forums on 7/12/2009


Franta,

The PCBE agent back end service name is APC PBEagent. Try starting this service and see if you get any error message.

Are you able to access the PCBE agent web interface? If so, Can you see the UPS information without an error through the Agent web interface?

The PCBE version 8.0.1 Single node version has only the Agent. The PCBE agent is only sufficient to monitor the UPS on your local Computer. The PCBE server and console are used to monitor two or multiple UPSs in a single console page.

See Answer In Context

Reply
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:39 AM

0 Likes
0
542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:39 AM

This reply was originally posted by Jonathan on APC forums on 7/12/2009


Hello Franta, welcome to the APC Forums.

Priot to having PCBE 8.0.1 on your system, would you happen to have previous version of PCBE on it? Also, can you provide the exact model and serial number of your UPS and the exact version of your Windows 2000 Server? If you do have previous version of PCBE did you uninstall all of the components like PCBE Agent, Server and Console?

The APC PowerChute Business Edition software offers UPS management and monitoring. In order for a certain customer to make some changes on the UPS they need to use that software and for us to prevent unauthorize access and configuration of the UPS we've provided a login page to the customer so that only those persons authorize can make some changes on it. Where are you getting the login problem is it on the PCBE Agent or Server? PCBE Agent can be accessed by opening a web browser and opening the address http://:3052 this can be done on the computer where you installed the agent or on another PC that is on the same network. If you are on the local PC you can also use http://127.0.0.1:3052. Once you are on the Agent interface try to login and see if you are getting any error message, if you are looping back on the same screen normally I suggest downloading the latest Java from www.java.com. Have you also tried setting up PCBE on a different computer but same UPS? We would appreciate if you could provide more information regarding your problem.

You can also manage your UPS by adding another device which is the APC Network Management Card. It enables your UPS to be managed and monitored over the network, instead of connecting the APC Management Cables you just need to provide a network cable and hook it up on the card.

Reply
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 08:39 AM

0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:39 AM

This was originally posted on APC forums on 7/12/2009


Franta,

The PCBE agent back end service name is APC PBEagent. Try starting this service and see if you get any error message.

Are you able to access the PCBE agent web interface? If so, Can you see the UPS information without an error through the Agent web interface?

The PCBE version 8.0.1 Single node version has only the Agent. The PCBE agent is only sufficient to monitor the UPS on your local Computer. The PCBE server and console are used to monitor two or multiple UPSs in a single console page.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc