APC-750 UPS self-test fail: wrong message

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
aharyo_apc
Crewman
Crewman
0 Likes
4
557

APC-750 UPS self-test fail: wrong message

This was originally posted on APC forums on 4/27/2011


I have APC-750 UPS monitored by PowerChute, and scheduled to run self-test every weekend. It's been several weeks keep sending a fail self-test message and need battery replacement. I have just replaced the battery couple of months ago. However, every time it send the fail self-test, I try to run the self-test manually, and it comes back to on-line. Any idea why is this happened or suggestion to make the message sends the right one? Thanks


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
557

Re: APC-750 UPS self-test fail: wrong message

This reply was originally posted by Angela on APC forums on 5/2/2011


did the RBC have a serial number on it so we can check its age?

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
557

Re: APC-750 UPS self-test fail: wrong message

This reply was originally posted by Jonathan on APC forums on 4/28/2011


Good day Ahar,

Aside from the message that you receive thru PowerChute, I would like to check if the UPS itself shows a solid red replace battery indicator? Also, have you tried changing the USB/Serial cable?

Was it replaced with a genuine APC battery as well?

aharyo_apc
Crewman
Crewman
0 Likes
0
557

Re: APC-750 UPS self-test fail: wrong message

This was originally posted on APC forums on 4/29/2011


Yes, it shows a solid red replace battery indicator. I replaced it with genuine APC battery, last time.
Never tried to change the monitoring cable, though.

BillP
Administrator Administrator
Administrator
0 Likes
0
557

Re: APC-750 UPS self-test fail: wrong message

This reply was originally posted by Jonathan on APC forums on 4/29/2011


When was the last time that you have changed the battery? Because if the message is accompanied by a solid replace battery led it only means that the battery is bad and needs to be replaced.

BillP
Administrator Administrator
Administrator
0 Likes
0
558

Re: APC-750 UPS self-test fail: wrong message

This reply was originally posted by Angela on APC forums on 5/2/2011


did the RBC have a serial number on it so we can check its age?