New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
AP9220 (Share-UPS Plus) & AP9606
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0106:00 AM. Last Modified: 2024-03-0512:02 AM
AP9220 (Share-UPS Plus) & AP9606
Posting this in case someone else runs into this issue..
It looks as though the AP9220 (Share-UPS Plus) is the predecessor model to the AP9225 (MasterSwitch Plus).
My original AP9220 & AP9606 combo came with aosxx and supxx. I upgraded to the latest aos for the AP9606: aos326b.bin. This wiped out the sup100b.bin app file. The supxxx.bin file/product tree is not available on APC's ftp site.
I had tried the msp200.bin app file before, but didn't work.. then stumbled on this: http://forums.apc.com/message/9580#9580. So, downgraded aos to 2.5.4 and tried msp200 again - worked like a charm: Share-UPS Plus is listed as a MasterSwitch Plus and web-based control works as expected.