Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AP8453 - Metered-by-Outlet - Total KwH by outlet

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP8453 - Metered-by-Outlet - Total KwH by outlet
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:21 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
5
3957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:21 AM . Last Modified: ‎2024-02-14 11:02 PM

AP8453 - Metered-by-Outlet - Total KwH by outlet

Hi

I have multiple AP8853, witch is metered PDU, but not by outlet.
Iam looking at AP8453, but just have some question about it?

What we will use it for is to count the power usage by our co location customer, and then bill them for the usage.

1. The one i have can tell me how much KwH the hole PDU have used, since it last reset.
Can the AP8453 tell me how much KwH, each outlet have taken since last reset? And can it tell me this though SNMP?
(As the AP8853, can tell me though SNMP how much KwH it have taken since it last reset though SNMP).

2. Can i reset just one outlet total KwH, or is the hole PDU i need to reset?

Regards Kenneth Dalbjerg

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Thx for reply.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
BillP Leader
Leader

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Hi,

1a.) Yes, at the outlet level, you can see current (amps), energy (kWh), and power (watts). Below is a screenshot from a PDU with metering by outlet:

XWeM0f296IpqnGScsn2OGA%3D%3D.pngXWeM0f296IpqnGScsn2OGA%3D%3D.png

1b.) Yes, this is available via SNMP. All of the AP8XXX series Rack PDU OIDs are within the APC PowerNet MIB and the .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 table (.1.3.6.1.4.1.318.1.1.26). If you browse this table, there are OIDs to see info at the outlet level, rPDU2Outlet.rPDU2OutletMetered.rPDU2OutletMeteredStatusTable .. and you'll find .rPDU2OutletMeteredStatusEnergy.

2.) Yes, you can reset energy (kWh) at the outlet level but it forces you to reset all outlets at the same time. You can also do this for power values.

8SwngX8PP7YoDs0W1g2vaQ%3D%3D.png8SwngX8PP7YoDs0W1g2vaQ%3D%3D.png

I say it this way because if I reset all of the kWh loads today: kJO1Wi1nFTMq8oPjxaqY%2BA%3D%3D.pngkJO1Wi1nFTMq8oPjxaqY%2BA%3D%3D.png

It does not reset kWh for the entire device (note it still has an earlier date): 

r%2FQe%2FlnnOZABgMl7MejrmQ%3D%3D.pngr%2FQe%2FlnnOZABgMl7MejrmQ%3D%3D.png

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Thx for you reply 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Are there any different if we buy the AP8653 instead of AP8453?
It support switching and i think that could be an cool thing to have 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Hi Kenneth,

No, AP8653 just adds switching/control of the outlets like you said. The Metering By Outlet functionality will be present and identical to what I explained previously. So, if you'd like to add that ability to control outlets, then go for the AP8653. It certainly can come in handy!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
3957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Thx for reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore