Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP4423 Possible open fuse Source A

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP4423 Possible open fuse Source A
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Spardha
Crewman Spardha
Crewman

Posted: ‎2022-01-27 05:51 AM

0 Likes
8
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-01-27 05:51 AM

AP4423 Possible open fuse Source A

Hi,

 

We had a power surge a few days ago and now I cannot clear this issue on the AP4423.  

 

Source A is mains UK power and Source B is UPS power.

 

I have removed the unit from the cab and plugged in else where but have the same issue, I cant see any external fuses that can be replaced.

 

Help!!

 

Thanks in advance.

Labels
  • Labels:
  • Datacenter Accessories
  • Rack Accessories & Cooling
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Spardha
Crewman Spardha
Crewman

Posted: ‎2022-01-31 03:20 AM

0 Likes
7
1861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-01-31 03:20 AM

Added an image from the unit, Source B is disconnected as it's been removed from the cabinet until this can be resolved

apc4423 error.JPG

  • Tags:
  • english
Reply
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-02 06:15 AM

In response to Spardha
0 Likes
6
1850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-02 06:15 AM

Hi

 

Just to be clear, you tried moving the ATS to different power sources, but the issue remained, with source B being unavailable?

If so, I am curious as to what version of the firmware you are running on the unit, and would you be able to share the support file from the unit?

-> https://www.apc.com/ie/en/faqs/FA156131/

The process described for NMC2 is applicable for this unit.

 

Best regards

Tonny

  • Tags:
  • english
Reply
Spardha
Crewman Spardha
Crewman

Posted: ‎2022-02-03 02:39 AM

In response to TonKei
0 Likes
5
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 02:39 AM

Hi,

 

Yes, I moved the APC from the CAB and plugged it in somewhere else in the building, I believe the server room is on its own circuit so I was hoping it would either clear the issue or give me an idea of the issue.

 

Serial Number
5A1838T68992

Firmware Version
4.1.9
Firmware Date
03/16/17
Downloader Version
4.3


Due to the issue, the APC has been taken out of the live cab as its not working anyway, but i have kept it plugged in to try and resolve it.

Attachments
  • Tags:
  • english
Reply
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-03 04:28 AM

In response to Spardha
0 Likes
4
1839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 04:28 AM

Hi

 

I think the next step should be to upgrade to latest firmware version for the unit, to ensure that is is not a software based issue.

You can find the firmware here -> https://www.se.com/ww/en/download/document/APC_ATS4G_704_EN/

 

After the reboot, I suggest doing a power-cycle of the unit.

 

If that does not help, you are most likely looking at a issue with the hardware, and in that case you should contact your local CCC in regards to a possible replacement under the warranty.

 

Best regards

Tonny

 

  • Tags:
  • english
Reply
Spardha
Crewman Spardha
Crewman

Posted: ‎2022-02-03 05:08 AM

In response to TonKei
0 Likes
3
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 05:08 AM

Doesnt seem to have worked. Although I haven't been able to power cycle due to not being on-site.

Attachments
  • Tags:
  • english
Reply
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-03 05:31 AM

In response to Spardha
0 Likes
2
1834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 05:31 AM

Hi

 

I think you might be looking at the wrong firmware there.

The firmware you are upgrading is the firmware for the Network management module in the unit.

 

If you navigate to [About] -> [Network] on the web interface, you can find the information under application module.

The version number presented there is the one you should be looking at.

 

Best regards

Tonny

  • Tags:
  • english
Reply
Spardha
Crewman Spardha
Crewman

Posted: ‎2022-02-03 05:35 AM

In response to TonKei
0 Likes
1
1832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 05:35 AM

I see, its now v7.0.4 but the error is still present.

  • Tags:
  • english
Reply
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-03 05:53 AM

In response to Spardha
0 Likes
0
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-02-03 05:53 AM

Hi 

 

In that case you are likely looking at a hardware issue.

I would suggest opening a case with your local CCC and get them involved, especially if the unit is under warranty.

 

Best regards

Tonny

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc