Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84804members
354257posts

ACRD602P ALARMS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

ETCO
Crewman
Crewman
0 Likes
4
470

ACRD602P ALARMS

We have an ACRD602P cooling unit in a datacenter that frequently gives these alarms:

 

- Humidifier Low Water Condition

- Humidifier Error Tolerance Exceed Condition

 

Knowing that three units of this type installed in datacenter and this is the only one gives this alarm.

 

Please any advice to solve the problem.

Tags (1)
4 Replies 4
EduardoE
Crewman Crewman
Crewman
0 Likes
3
462

Re: ACRD602P ALARMS

Have You checked the water supply line for the humidifier to see if it's receiving water pressure, from the city water? What is the current humidity value? And setpoint? In order to better assist You on this one.

Tags (1)
ETCO
Crewman
Crewman
0 Likes
2
441

Re: ACRD602P ALARMS

Hi,

 

The Humidifier and Dehumidifier were disabled but we always get these alarm, the unit was working from 2018 and there is no problem, a couple of weeks ago we start getting these messages.

Tags (1)
EduardoE
Crewman Crewman
Crewman
0 Likes
1
416

Re: ACRD602P ALARMS

Please reach us at:  877-287-7835 (Opt. 2 Opt. 2). Cooling Technical Support In order to better troubleshoot this.

Tags (1)
EduardoE
Crewman Crewman
Crewman
0 Likes
0
389

Re: ACRD602P ALARMS

Hello Mahmoud. The case# 84499130 has been created for You. I'll reach You by email. For follow up. 

Tags (1)