have a site where input voltage goes up to 127V. get frequent alerts stating "UPS: compensating for high input voltage". would like to change the threshold to 128V before alerting. How do i make that change?
management card: UPS Network Management Card 2
UPS: Smart-UPS 2200
firmware: ID18UPS 08.8
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:58 AM . Last Modified: 2024-03-08 04:39 AM
Hi Nathan
You can change the low and high transfer points to control at what input voltage the UPS will transfer to battery.
The alert you are getting appears to be the UPS notifying you that it is using the AVR to trim the voltage down to an acceptable level. This isn't something that can be altered.
However you can remove it from the list of events on your NMC log and if you are receiving it in emails going to
Configuration / Notification / Event Actions / By Event / Input Line Status
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 03:58 AM . Last Modified: 2024-03-08 04:39 AM
Hi Nathan
You can change the low and high transfer points to control at what input voltage the UPS will transfer to battery.
The alert you are getting appears to be the UPS notifying you that it is using the AVR to trim the voltage down to an acceptable level. This isn't something that can be altered.
However you can remove it from the list of events on your NMC log and if you are receiving it in emails going to
Configuration / Notification / Event Actions / By Event / Input Line Status
Regards
Matt