have a SU1500 which would not show any events (actually did show 2 from 2 months ago)
but hasn't shown anything since then such as undervoltages (when lights in office dim)
or power outages (when i pulled the plug). Reset the sampling interval from 2 hours to 1
minute (per APC support) and it, at least, showed an event when I pulled the plug after
the change. i do not understand why changing the sampling interval would affect the event
log. Any thoughts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:31 AM
It shows on the log that you have provided earlier, the UPS is utilizing the Green Mode feature. The Green Mode feature gets activated once the unit has detected that you have clean and good input voltage and frequency, thus eliminating the need to use the UPSs other components such as voltage regulation and filtering. With regards to the other UPS being able to detect power outages, can you check both UPS and see if the Power Quality are set the same i.e. Low, Medium or High.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:46 PM . Last Modified: 2024-03-11 04:31 AM
APC Smart-UPS SMT1500 1500VA 120V LCD UPS System
Agent: 9.0.1.606
Windows Server 2008 6.0
UPS Model Smart-UPS 1500
Firmware UPS 08.3 / MCU 14.0
these are the logs from the software (the lights in the office all dimmed significantly this morning).
3/12/13 | 10:33:38 | Online (Green Mode) - Entered |
3/12/13 | 09:05:21 | Online (Green Mode) - Exited |
3/6/13 | 07:42:08 | Online (Green Mode) - Entered |
3/6/13 | 07:42:07 | Communication Established |
how do i check the event logs on the LCD? (Unfortunately, the unit is in Georgia and
i am in virginia).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:46 PM . Last Modified: 2024-03-11 04:31 AM
Sorry, need to add some more information. i bought another unit and it seems to catch
power outages in the event log but does not catch under voltages (unless we are getting
odd problems on internal circuits and not the the feed). So I have two questions and the
first is why would the event log be affected by the sampling interval (problem noticed
on the first unit) and, second, why isn't the second unit catching these voltage fluctuations
(and the first didn't seem to catch them either)? Sorry if i am making this more complex
than it needs to be but i really didn't like leaving the first UPS on the server when it was
at an out of town location. thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:31 AM
Can you confirm the model number of your UPS please? Also, is it the event logs on the LCD or the logs from the software i.e. PowerChute Business or Network Shutdown that you are having problems with?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:47 PM . Last Modified: 2024-03-11 04:31 AM
It shows on the log that you have provided earlier, the UPS is utilizing the Green Mode feature. The Green Mode feature gets activated once the unit has detected that you have clean and good input voltage and frequency, thus eliminating the need to use the UPSs other components such as voltage regulation and filtering. With regards to the other UPS being able to detect power outages, can you check both UPS and see if the Power Quality are set the same i.e. Low, Medium or High.
Link copied. Please paste this link to share this article on your social media post.