I have two Smart UPS. First is a SMX1500RM2UNC and the other is a SMT1500. Both have the AP9631 Network Card.
The AP9631 is running the version 6.4.
Is there a way to change the name so when I am on the Web UI, instead of listing the following at teh top of the screen it has a custom name. right now it lists:
UPS Network Management Card 2
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:14 PM . Last Modified: 2024-03-06 11:19 PM
thanks for the response. I will create dedicate email addresses for each to change the from address and give that a try.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:14 PM . Last Modified: 2024-03-06 11:19 PM
Hi Mike,
Unfortunately, you cannot modify the two locations you referenced. For the first question on the web UI, we are working on adding the hostname display somewhere on the web page. For now, I don't have a great answer. The home page tells you but that is it beyond the hostname or IP address in the URL bar in the browser (assuming you have that showing.) But, we are working on adding this as I noted.
Regarding the emails, the only thing you can customize which I recommend is the "From" address that the email will appear to be coming from. Within the email itself too, it will show the properties of the NMC and UPS inside (name, serial number, etc) but I understand that means opening or previewing the email. I recommend the "From" address tweak though if it is able to be modified. Depending on what email service you use, it may not be able to be modified, especially services like GMail, Yahoo, etc.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:14 PM . Last Modified: 2024-03-06 11:19 PM
thanks for the response. I will create dedicate email addresses for each to change the from address and give that a try.