Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82448members
349986posts

Smart-UPS RT 8000 Red Led

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
ITDesk_apc
Cadet
0 Likes
1
174

Smart-UPS RT 8000 Red Led

This was originally posted on APC forums on 8/1/2018


Goodmorning,

We have a Smart-UPS RT 8000 that beeps every few seconds. The RED led blinks most of the time but sometimes it is Solid RED.

I guess one of the battery's is dead, but how do I know which one?

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
174

Re: Smart-UPS RT 8000 Red Led

This reply was originally posted by Liam on APC forums on 8/1/2018


Yes, that would indicate that you have a bad battery. All 4 battery modules must be replaced at the same time. The replacement battery kit part number is APCRBC140, which contains 2 modules. You would need to purchase two of the APCRBC140 kits to get all 4 modules.

Thanks,

Liam

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
175

Re: Smart-UPS RT 8000 Red Led

This reply was originally posted by Liam on APC forums on 8/1/2018


Yes, that would indicate that you have a bad battery. All 4 battery modules must be replaced at the same time. The replacement battery kit part number is APCRBC140, which contains 2 modules. You would need to purchase two of the APCRBC140 kits to get all 4 modules.

Thanks,

Liam