Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82165members
349734posts

Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
atamgp_apc
Crewman
Crewman
0 Likes
4
555

Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This was originally posted on APC forums on 9/5/2012


Hi, i'm new to ups diagnostics 🙂 and this is my first problem. I will try to explain the problem brief but complete and supply with enough information.

The ups has been bought 2nd hand as a try-out for my new home business. It has feeded my dual socket server for almost a year. It has a date of 2006 and the original batteries are still being used (see pictures). I don't mind replacing the batteries ..... if that is needed to be done.

problem: It does not start. If i power the ups, it will start with the self test. Here the "online" led will go on first, followed by a blinking "on battery" led going over to a red non-blinking "overload" led with a disgusting background sound. So i switch it of to stop the sound. The ups is partly on but no green lights. he 2 fans are on and i can connect to the ups hence the supplied pictures. No hardware is connected to the ups , so no load....

i tried: brain dead option, removed the battery connection inside and connected again, nothing helped.

Info:
ups model: smart-ups 1500 xlm
serial number: QS0645320159
manufacture date: 23-9-2006
firmware rev: 716.3.1
battery replaced: 23-9-2006

ups status: unknown
internal temp: 24,7 C / 76,5 F
output voltage: 0 vac
input voltage: 227,5 vac
output freq: 50 hz
load power: 3,9 % va
load current: 0 A

battery status: Normal
battery voltage: 54,54 VDC
Runtime remaining: 205 min
battery replaced: 23-9-2006
battery pack count: 0
battery charge: 99%


ups self-test
last self test: 4-9-2012
result: failed

ups-calibration: unable to do this...
cal. date: unknown
cal. result: unknown


Can someone help me diagnose the problem?
Is there something like a fuse?
Thanks in advance...

Attachments

Accepted Solutions
Battman_apc
Commander
Commander
0 Likes
0
555

Re: Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This was originally posted on APC forums on 10/1/2012


The XLM model allows removal of the inverter/charger/controller module (right side of ups om rack mount orientation) ....if you remove the screws on the front (philips screwdriver) flip over the little tab lever at the bottom left you can pull out the module. Have you tried that step to refresh the electrical connections between the module and the ups cabinet (frame) ?

Message was edited by: Battman

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
555

Re: Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This reply was originally posted by Bernard on APC forums on 9/5/2012


Hi! Are you sure that its the Overload LED that's lit? Because if it is, it may indicate an internal fault (that is if there is no load attached). If it's not, and it is the Replace Battery LED (the one that looks like a battery with an "X" inside it) that is lit solid and accompanied by rapid beeping after the selftest then it's just the batteries that need to be replaced.
[You can get the batteries here|http://www.apc.com/tools/upgrade_selector/index.cfm]

BillP
Administrator Administrator
Administrator
0 Likes
0
555

Re: Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This reply was originally posted by Angela on APC forums on 9/5/2012


also, are you using both powerchute business edition AND a network management card? i ask because you are showing screenshots of the PCBE interfaces and then you show a screenshot of putty which is a network management card screen (since this UPS comes pre-installed with one). you should only be using one or the other technically so if I had to suggest one, it should be the network management card.

I would disconnect the serial cable and either terminal in or web in to the network management card to set it up and i need to review the logs in there which would be extremely helpful in diagnosing this issue with you.

here are some knowledge base articles to help you:

• How to set up the network management card with an IP address: http://www.apc.com/support/index?page=content&id=FA156064

• How to download the event.txt, data.txt, and config.ini (which I'd like to see - feel free to remove any private info): http://www.apc.com/support/index?page=content&id=FA156131

if you can post those logs here, it should help greatly.

atamgp_apc
Crewman
Crewman
0 Likes
0
555

Re: Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This was originally posted on APC forums on 9/6/2012


ok, thanks for the replies.

I will see into the logs and post them. The link you supplied is down currently ... i have to wait.

Yes, the overload led is on. And also now the Bypass led is on together.......

Battman_apc
Commander
Commander
0 Likes
0
556

Re: Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

This was originally posted on APC forums on 10/1/2012


The XLM model allows removal of the inverter/charger/controller module (right side of ups om rack mount orientation) ....if you remove the screws on the front (philips screwdriver) flip over the little tab lever at the bottom left you can pull out the module. Have you tried that step to refresh the electrical connections between the module and the ups cabinet (frame) ?

Message was edited by: Battman