Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82473members
350045posts

SURTD and SURT adjusting sensitivity. It's possible?

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
5
213

SURTD and SURT adjusting sensitivity. It's possible?

This question was originally posted by Federico on APC forums on 4/22/2010


Is there any way of adjusting in put voltage sensitivity and frequency in Smart RT series UPS?

It's there a difference between the SURTD5000XLI and SURT5000XLI that would a affect UPS behavior while running under a genset?

The thing is that the old model worked fine till it cracked and the new one, the D series runs into battery for a brief instant every time a load is turned on.

Could be this a some common failure with the UPS? Or its just a Genset problem? Geny: Onan 4.8kW QD 5000 diesel.


Thanks!


Accepted Solutions
jjuls_apc
Crewman
Crewman
0 Likes
0
213

Re: SURTD and SURT adjusting sensitivity. It's possible?

This was originally posted on APC forums on 9/20/2011


Clarkson,

I need help. Our model is SURTD5000XLT. Can the input voltage and frequency be adjusted. We are using a 13000 watts
generator but with fluctuating voltage. 195 to 206 V AC. Can the UPS be adjusted to adopt to this fluctuation.

Thanks in advance

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
213

Re: SURTD and SURT adjusting sensitivity. It's possible?

This reply was originally posted by Federico on APC forums on 4/29/2010


Thanks! Do you know what is the pulse-rectifier setting for the Smart RT series UPS?

jjuls_apc
Crewman
Crewman
0 Likes
0
214

Re: SURTD and SURT adjusting sensitivity. It's possible?

This was originally posted on APC forums on 9/20/2011


Clarkson,

I need help. Our model is SURTD5000XLT. Can the input voltage and frequency be adjusted. We are using a 13000 watts
generator but with fluctuating voltage. 195 to 206 V AC. Can the UPS be adjusted to adopt to this fluctuation.

Thanks in advance

jjuls_apc
Crewman
Crewman
0 Likes
0
215

SURTD and SURT adjusting sensitivity. It's possible? SURTD5000XLT

This was originally posted on APC forums on 9/20/2011


Clarkson,

Is there a difference between XLI and XLT?
I need help on adjusting the input voltage and frequency for this model.
The 13000 watts generator out voltage is 195 to 206 V ac. How do I adjust the UPS to make it adopt to this input range?

Thanks

BillP
Administrator Administrator
Administrator
0 Likes
0
215

Re: SURTD and SURT adjusting sensitivity. It's possible? SURTD5000XLT

This reply was originally posted by Angela on APC forums on 9/20/2011


XLI is a 230v international model and XLT is a north american model that is designed for 208v or 240v.

on the 230v, it is designed for a phase, neutral and ground connection for a single phase connection. the north american model is used with two phases and a ground connection.

if there is an option to change the output, you can do it via the network management card or RT control menu most likely. do you have the NMC set up? if not, you can set that up or plan on directly connecting to the RT with a serial cable.

BillP
Administrator Administrator
Administrator
0 Likes
0
215

SURTD and SURT adjusting sensitivity. It's possible?

This reply was originally posted by Federico on APC forums on 4/22/2010


Is there any way of adjusting in put voltage sensitivity and frequency in Smart RT series UPS?

It's there a difference between the SURTD5000XLI and SURT5000XLI that would a affect UPS behavior while running under a genset?

The thing is that the old model worked fine till it cracked and the new one, the D series runs into battery for a brief instant every time a load is turned on.

Could be this a some common failure with the UPS? Or its just a Genset problem? Geny: Onan 4.8kW QD 5000 diesel.


Thanks!