Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82478members
350056posts

SUA3000XRT output amp confusion

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
48

SUA3000XRT output amp confusion

This question was originally posted by Glenn on APC forums on 3/10/2009


IHAC who's building electrician is advising them against a SUA3000XRT UPS that they just received. The input is a NEMA 6L-20P. Two of the four outputs are NEMA 6L-30R. He states that you can't use 30 amp outputs when you only have a 20 amp input. It makes sense to me but I'm not completely savvy to the internals of a UPS and whether they can provide these tow 30 amp circuits or not. It seems odd that there would be this configuration if it wasn't sound. Any help in explaining this will be greatly appreciated.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
48

Re: SUA3000XRT output amp confusion

This reply was originally posted by Oscar on APC forums on 3/11/2009


The L6-30 receptacles are still rated for 20 amps. The amperage on the output is limited to the input plug type. These units were made with L6-30 receptacles so that you can connect our stepdown transformers to provide 120V. Our generic stepdown transformers has an L6-30P for the input, being that this is a 208 V UPS, having L6-30 receptacles makes this compatible configuration ideal.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
49

Re: SUA3000XRT output amp confusion

This reply was originally posted by Oscar on APC forums on 3/11/2009


The L6-30 receptacles are still rated for 20 amps. The amperage on the output is limited to the input plug type. These units were made with L6-30 receptacles so that you can connect our stepdown transformers to provide 120V. Our generic stepdown transformers has an L6-30P for the input, being that this is a 208 V UPS, having L6-30 receptacles makes this compatible configuration ideal.