Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82468members
350031posts

Replace battery icon on new Backup pro 1500

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
angeldr_apc
Crewman
Crewman
0 Likes
1
150

Replace battery icon on new Backup pro 1500

This was originally posted on APC forums on 10/15/2013


I received a new Backup pro 1500 yesterday. Now, when I turn  off the backup, the icon "replace batery"  show.

What happens??

Also, the error F02 ever show when the backup work on battery mode.

Thank you very much for your help.

AngelDR.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
152

Re: Replace battery icon on new Backup pro 1500

This reply was originally posted by Angela on APC forums on 10/15/2013


F02 is explained here ->http://www.apcmedia.com/salestools/EALN-7V5MXA/EALN-7V5MXA_R1_EN.pdf

Regardless, this is a battery issue and before we get too concerned, you need to let the UPS charge up for about 24 hours to eliminated a discharged battery as the root problem.

If you have frequent power outages that can disrupt charging while the UPS is on, please turn the UPS off but leave it plugged in for at least 24 hours without touching it and then go ahead and turn it back on after the 24 hours to ensure the battery is charged. Then, I'd see if you still have a replace battery indicator and F02.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
153

Re: Replace battery icon on new Backup pro 1500

This reply was originally posted by Angela on APC forums on 10/15/2013


F02 is explained here ->http://www.apcmedia.com/salestools/EALN-7V5MXA/EALN-7V5MXA_R1_EN.pdf

Regardless, this is a battery issue and before we get too concerned, you need to let the UPS charge up for about 24 hours to eliminated a discharged battery as the root problem.

If you have frequent power outages that can disrupt charging while the UPS is on, please turn the UPS off but leave it plugged in for at least 24 hours without touching it and then go ahead and turn it back on after the 24 hours to ensure the battery is charged. Then, I'd see if you still have a replace battery indicator and F02.