Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82179members
349776posts

Raise the voltage at which the UPS activates?

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
brown_apc
Cadet
0 Likes
1
96

Raise the voltage at which the UPS activates?

This was originally posted on APC forums on 7/12/2013


Hello - Is there a way to configure the PowerChute software so that the battery backup will engage when the voltage drops below 100V? In the software the highest voltage is 88V.  I'm running an Backup-UPS Pro 1500.   Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
96

Re: Raise the voltage at which the UPS activates?

This reply was originally posted by Angela on APC forums on 7/15/2013


Your UPS should have a voltage transfer range setting you can adjust. All of the settings for that come from the UPS and not the software itself. The software just gives you an interface to change the settings on the UPS.

Also, this UPS has automatic voltage regulation (AVR). To prevent using your UPS battery, the AVR is designed to kick in when you have voltages below 120V (or whatever the nominal voltage is). When the transformer is no longer able to boost the voltage to an acceptable level, then the UPS transfers to battery. Higher than 88V, the AVR will kick in and boost your voltage and save battery life.

Per the user's guide:

Online Input Voltage Range           88 - 139V

Automatic Voltage Regulation      (94-107V) +11.5% (boost)

                                                 (126-141V) -11/5% (trim)             

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
97

Re: Raise the voltage at which the UPS activates?

This reply was originally posted by Angela on APC forums on 7/15/2013


Your UPS should have a voltage transfer range setting you can adjust. All of the settings for that come from the UPS and not the software itself. The software just gives you an interface to change the settings on the UPS.

Also, this UPS has automatic voltage regulation (AVR). To prevent using your UPS battery, the AVR is designed to kick in when you have voltages below 120V (or whatever the nominal voltage is). When the transformer is no longer able to boost the voltage to an acceptable level, then the UPS transfers to battery. Higher than 88V, the AVR will kick in and boost your voltage and save battery life.

Per the user's guide:

Online Input Voltage Range           88 - 139V

Automatic Voltage Regulation      (94-107V) +11.5% (boost)

                                                 (126-141V) -11/5% (trim)