I have been measuring 9 - 10 volts AC from neutral to ground on the output of this UPS. The input voltage (neutral to ground) is only 2 volts AC. Any recommendation on how to fix this? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
you're welcome 🙂 thank you to my UPS engineer. lol
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
is this while online or on battery?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
This is while online. I haven't measured it while on battery. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
hello again..i was not sure so i asked someone who works with UPSs and they told me this:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
Good explanation! Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:10 AM . Last Modified: 2024-03-13 01:02 AM
you're welcome 🙂 thank you to my UPS engineer. lol