Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82169members
349762posts

PowerChute network shutdown and power failure simulation

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
189

PowerChute network shutdown and power failure simulation

This question was originally posted by Philippe on APC forums on 5/30/2017


Hello, I realize the reconfiguration of a Smart-ups 5000 with a management card AP9630 (with sumx 6.4.6) and powerchute network shutdown. I added a test agent and I would like to simulate a power failure to verify that the powerchute configuration is operational before adding other agents.

Is there a way to do this simulation without disrupting the rest of the diet?

Thank you in advance.
Philippe

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
189

Re: PowerChute network shutdown and power failure simulation

This reply was originally posted by Bill on APC forums on 5/30/2017


Hi,

To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
190

Re: PowerChute network shutdown and power failure simulation

This reply was originally posted by Bill on APC forums on 5/30/2017


Hi,

To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.