This reply was originally posted by Angela on APC forums on 10/6/2016
Hi Adrian,
Can you follow this post and check the firmware and post a screenshot as I asked that poster to do?
http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/13097/conec...
Also, did you ever use or touch the USB port on the back of the SUA? This will "kill" /disable the serial port which the serial port/bus is where the AP9630, AP9610, and AP9600 are all operating. If this is the case, whether it happened because you used USB or the UPS needs a reset on its serial bus, you'd need to do the following:
- Turn off any attached load to the UPS. (You don't have to unplug the items.)
- Unplug the UPS itself from AC power - so unplug the UPS from the wall.
- You need to press and hold down the off button on the front of the UPS which looks like this: (o) Press and hold it for at least 5 seconds and if the previous step was done, the UPS should click and flash its from panel LEDs. This resets the serial communications within the unit.
- You can then plug the UPS back into AC power, turn it back on and turn your equipment back on. Then check the status in the AP9630. Side note: you have that connected properly. Due to the required installation priority of the accessories, so they can operate properly on the serial bus, AP9610 should be in the UPS (lower priority) and the AP9630 should be in the AP9600.
We can also check the firmware versions out just in case before you do all that. Since you already rebooted the NMC, we can rule that out. I assume though, "repowering the UPS" did not include the specific required sequence I mentioned above? Turning the UPS on/off with the power button does not reset the communications like the "braindead" procedure steps I listed above.