I have APC Smart-UPS 2200VA LCD 230V (SMT2200I) with AP9631 and before the firmware update, everything was fine.
After the update, I have "Lost Communication to the UPS".
Could you help me, please?
Thanks,
Nik
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-17 09:14 AM
Hi @NikSpasov,
Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.
The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...
As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.
Regards,
Shaun
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-17 09:14 AM
Hi @NikSpasov,
Thanks for the screenshot, it makes getting to the issue much easier - the screenshot shows the firmware loaded is "sy3p", which is for 3-Phase Symmetra UPS - so the card is complaining because it's trying to speak to a Symmetra, and a Symmetra isn't answering.
The current firmware for your UPS would be https://www.se.com/ie/en/product/SFSUMX704/ups-network-management-card-v7-0-4-firmware-for-smartups-...
As the card still appears to be on the network, recovery should be as simple as loading the correct firmware.
Regards,
Shaun
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-17 10:51 AM . Last Modified: 2022-01-18 12:07 AM
Thank you very much, @Shaun,
Somehow, I successfully killed the network card.
I have downloaded this: file apc_hw05_aos704_sumx704_bootmon109.exe
In the middle of installation, the tool lost connection to UPS. (FTP method)
Now I can't find the network card anymore.
Do you have any idea how to fix this mess?
Thanks
Nik
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-22 02:15 PM
Where its possible download prev. versions of firmware? I update to 7.1.2, and I got same trouble Lost Communication to the UPS...
thanks a lot