Posted: 2021-06-30 12:20 AM . Last Modified: 2024-03-11 04:09 AM
Hi everyone,
Just one SMX1500RM2UNC isn't recording ambient into data log; universal IO sees sensor just fine? I have many other units, identical model and AP firmware and they record it just fine. This one - the column is blank? All run the latest firmware 6.5.0 and have identical AP9631
Any ideas? Rebooted the AP many times in a hope to kick start it - no go, still T1ambC is blank?
Mike Thanks Mike, I did absolutely nothing and when I checked just now it has started working. Wierd...
Hi Boyan,
Is this the temp probe that came with the NMC?
Could you also verify the UPS fw version. You can find this under About > UPS.
A few steps that you can try:
1. Try to move the temp probe to a diff IO port then reboot the NMC after moving.
2. Format the card to factory setting but leave the IP. This can be found under Control > Network > Reset/Reboot > Reset All (put a check on Exclude TCP/IP)
3. Try a different temp probe.
4. Try to move the NMC to a different UPS and see if issue follows.
5. Try to move the temp probe to a diff UPS and see if the issue follows.
If everything else fails, you may want to call tech support for further diagnosis and potential replacements if under warranty.