Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82408members
349915posts

Issues with loading web GUI after upgrading AP7911A

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

geraldoleonardo
Crewman
Crewman
0 Likes
1
204

Issues with loading web GUI after upgrading AP7911A

I tried to upgrade AP7911A and now can not access the web page anymore

I get the following error

 

mhv3aXs

 

 

How do i get out of this? Can i reset the PDU and be able to access the web GUI again?

Tags (1)
1 Reply 1
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
144

Re: Issues with loading web GUI after upgrading AP7911A

Hello

 

This could be an application module that is not loading.

 

Can you access the unit via SSH or telnet?

If so, you will be presented with status information right after logging in.

It should look something like this:

Untitled.png

 

 

 

 

The PNA status is the relevant bit here, and they should all have a "+" after the letter.

If the A is followed by a "-" or a "!" the application module is not running correctly and the web will not function.

 

If this is the case, I would suggest downloading the latest version of the firmware and flash it again.

 

 

Best regards

Tonny