As i see on the status page of Smart-UPS RT 3000 XL, it shows that the battery voltage is 217.3 VDC. I also used voltage meter on extended battery terminal and the voltage is 217.3 vdc! I wanted to use bigger battery, and i have 4 of them 150amp each! How they can be use on with such a high voltage?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:18 AM . Last Modified: 2024-03-18 11:23 PM
Hi,
The Smart-UPS is not designed to work in that configuration. If you attach any batteries to the UPS that have not be tested and approved by Schneider Electric you will void any remaining warranty and you could damage the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:18 AM . Last Modified: 2024-03-18 11:23 PM
Hi,
The Smart-UPS is not designed to work in that configuration. If you attach any batteries to the UPS that have not be tested and approved by Schneider Electric you will void any remaining warranty and you could damage the UPS.