Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82414members
349922posts

Frequency output on SURT10000RMXLI

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
vvv850_apc
Crewman
Crewman
0 Likes
3
133

Frequency output on SURT10000RMXLI

This was originally posted on APC forums on 8/2/2013


Hello,

I am trying to better understand the reason for having the option to select between +/- 0.1 and +/- 3 Hz for output frequency.

Currently our UPS is set to auto and is powering our server Rack. The nominal frequency in our country is 50Hz. We also have a backup generator which has an output frequency between 52Hz and 50Hz depending on the load.

Everything works well even on the genset but I wanted to know what are the implications of setting the output frequency to 50 +/- 0.1 or 50 +/- 3 from auto. Why would anyone want +/- 3 Hz output?

Regards.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
133

Re: Frequency output on SURT10000RMXLI

This reply was originally posted by Angela on APC forums on 8/2/2013


Did some more checking.

This option would also give you a broader range of when bypass operation would be available. If the frequency is "out of range" for bypass functionality and the UPS needs to go to bypass due to a fault or overload, it will drop the load.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
133

Re: Frequency output on SURT10000RMXLI

This reply was originally posted by Angela on APC forums on 8/2/2013


I think it just really depends on the install environment and load attached as far as how narrow or wide a user wants to allow their output frequency to fluctuate.

vvv850_apc
Crewman
Crewman
0 Likes
0
133

Re: Frequency output on SURT10000RMXLI

This was originally posted on APC forums on 8/2/2013


Ok, but why let the user decide the range of the output frequency if it is better to have a narrow fluctuation of +/- 0.1Hz than a wider +/- 3Hz frequency without any other considerations.

The reason I am asking is that I believe that there must be something to take into account if for example you have an output setting of +/- 0.1 Hz and suddenly your input goes above reaching 52Hz as when using a generator without too much load. Then the UPS should continue outputting 50 +/- 0.1 Hz but maybe? not be in online mode anymore thus not conditioning the output voltage.

BillP
Administrator Administrator
Administrator
0 Likes
0
134

Re: Frequency output on SURT10000RMXLI

This reply was originally posted by Angela on APC forums on 8/2/2013


Did some more checking.

This option would also give you a broader range of when bypass operation would be available. If the frequency is "out of range" for bypass functionality and the UPS needs to go to bypass due to a fault or overload, it will drop the load.