APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:53 AM . Last Modified: 2024-03-13 04:32 AM
I bought a few used 9617 network management cards, but I can't seem to set the IP on them.
I get a green status light on the two I tried, but the utility software cannot find them and they don't show up in my router.
I tried arp in Linux and Windows and it seemed to work, but when I try to Ping with 113 bytes of data it times out. I turned off the firewall in Windows, but it did not make a difference.
Any bright ideas? I might try a different UPS, but I don't think that's the issue. I gather I can connect the card directly to my laptop and try the utility software from there?
TIA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:54 AM . Last Modified: 2024-03-13 04:32 AM
Problem solved, I was able to get in through Putty once I remembered to turn off PowerChute. The default password was changed and the IP was some corporate IP range. So it's no wonder the utility could not find it, but I still don't know why arp did not work. Anyway I'm able to get in through the browser now, so on to the next problem of setting up my Linux boxes to talk to the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:54 AM . Last Modified: 2024-03-13 04:32 AM
Problem solved, I was able to get in through Putty once I remembered to turn off PowerChute. The default password was changed and the IP was some corporate IP range. So it's no wonder the utility could not find it, but I still don't know why arp did not work. Anyway I'm able to get in through the browser now, so on to the next problem of setting up my Linux boxes to talk to the UPS.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.