Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82246members
349809posts

Can I connect an AP7921 to a SURT003 with an AP9871?

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
Justchillin_apc
Cadet
0 Likes
1
103

Can I connect an AP7921 to a SURT003 with an AP9871?

This was originally posted on APC forums on 10/14/2009


I'm checking whether I can connect an AP7921, which has an IEC-320 C20 socket, to the NEMA L6-20R socket on a SURT003 using the AP9871 cable.

My main concern is the outlet on the SURT003 is rated 20A and the cable and rack PDU is rated 16A. Will the PDU only draw what it needs from the socket? I'm just making sure before I do this as I don't want to fry anything.

Thanks in advance for the advice.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT003

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7921

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9871

Message was edited by: Justchillin

Tags (2)

Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
103

Re: Can I connect an AP7921 to a SURT003 with an AP9871?

This was originally posted on APC forums on 10/14/2009


The PDU and cable ratings are downrated in accordance with the NEC "80%" rule, which brings a 20a device current rating to 16a. The PDU plugged into the SURT003 will be fine, as the PDU will only pull its own max draw, which won't cause an issue with the SURT003's outlet.

See Answer In Context

1 Reply 1
Erasmus_apc
Sisko
Sisko
0 Likes
0
104

Re: Can I connect an AP7921 to a SURT003 with an AP9871?

This was originally posted on APC forums on 10/14/2009


The PDU and cable ratings are downrated in accordance with the NEC "80%" rule, which brings a 20a device current rating to 16a. The PDU plugged into the SURT003 will be fine, as the PDU will only pull its own max draw, which won't cause an issue with the SURT003's outlet.