Having a cable ladder (6") installed by APC between NetShelters, across a "cold" aisle. Learned something new today--the installer from APC says they install them with the rungs on the top.
I looked at the documentation and it shows the rungs on top:
http://sturgeon.apcc.com/techref.nsf/partnum/990-1576A/$FILE/990-1576A-EN.pdf
however the submittal drawing shows the rungs on the bottom:
http://www.apcmedia.com/salestools/ASTE-6BFNZW_R1_EN.pdf
In a reply to a different post about racks in the forum Data Center Design » Architectural Design:
http://forums.isxusergroups.com/thread.jspa?threadID=137&tstart=0
a tip I got to improve the appearance was to line the ladder with "fish paper" liner (vulcanized insulating paper) so that you do not have to look up at the cables. I guess for this you would have to put the rungs on the bottom.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:29 AM . Last Modified: 2024-03-18 11:14 PM
Having a cable ladder (6") installed by APC between NetShelters, across a "cold" aisle. Learned something new today--the installer from APC says they install them with the rungs on the top.
I looked at the documentation and it shows the rungs on top:
http://sturgeon.apcc.com/techref.nsf/partnum/990-1576A/$FILE/990-1576A-EN.pdf
however the submittal drawing shows the rungs on the bottom:
http://www.apcmedia.com/salestools/ASTE-6BFNZW_R1_EN.pdf
In a reply to a different post about racks in the forum Data Center Design » Architectural Design:
http://forums.isxusergroups.com/thread.jspa?threadID=137&tstart=0
a tip I got to improve the appearance was to line the ladder with "fish paper" liner (vulcanized insulating paper) so that you do not have to look up at the cables. I guess for this you would have to put the rungs on the bottom.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:29 AM . Last Modified: 2024-03-18 11:14 PM
Thanks. We turned the ladder over to have the rungs on the bottom.
I did open an online APC support question just to see what they would say: I just got a one line answer back--to put the rungs on top.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:29 AM . Last Modified: 2024-03-18 11:14 PM
Having a cable ladder (6") installed by APC between NetShelters, across a "cold" aisle. Learned something new today--the installer from APC says they install them with the rungs on the top.
I looked at the documentation and it shows the rungs on top:
http://sturgeon.apcc.com/techref.nsf/partnum/990-1576A/$FILE/990-1576A-EN.pdf
however the submittal drawing shows the rungs on the bottom:
http://www.apcmedia.com/salestools/ASTE-6BFNZW_R1_EN.pdf
In a reply to a different post about racks in the forum Data Center Design » Architectural Design:
http://forums.isxusergroups.com/thread.jspa?threadID=137&tstart=0
a tip I got to improve the appearance was to line the ladder with "fish paper" liner (vulcanized insulating paper) so that you do not have to look up at the cables. I guess for this you would have to put the rungs on the bottom.