Hi,
Battery has died in one of our SURT3000XLI, we would like to order and replace it for new one, but unfortunately:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=RBC44&ISOCountryCode=gb
are now discontinued.
We found that:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=APCRBC140
looks indetical, so the question is: are they compatible?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:19 AM . Last Modified: 2024-03-18 11:22 PM
Yes, APCRBC140 is what you should use and it will be fine. Here is further information and detail on that topic for your reference -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA242324
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:19 AM . Last Modified: 2024-03-18 11:22 PM
Yes, APCRBC140 is what you should use and it will be fine. Here is further information and detail on that topic for your reference -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA242324