Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82446members
349982posts

Are these setting s correct?

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
274

Are these setting s correct?

This question was originally posted by Paul on APC forums on 7/22/2019


I think I have it set correctly but wanted to post here to be sure. I want the computer to run for one hour on battery, then initiate a shutdown. Do these settings look ok? I'm concerned because at the bottom it says "after 0 seconds the operating system shutdown starts"

 

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
275

Re: Are these setting s correct?

This reply was originally posted by Bill on APC forums on 7/24/2019


On 7/23/2019 4:39 PM, Paul said:

What if I choose "Do not shut down when power fails" and then under "Operating system and application shutdown" I put 600 seconds? Will it run until there are 600 seconds left on battery and then shutdown the machine?

When a Power Outage occurs:
The shutdown process will not start until the remaining UPS runtime falls below the combined time configured for Application and Operating System shutdown. If you set the OS shutdown to 600 seconds when the runtime falls below 600 seconds a shutdown will be triggered.

 

See Answer In Context

Attachments
4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
276

Re: Are these setting s correct?

This reply was originally posted by Bill on APC forums on 7/23/2019


Hi,

PowerChute will initiate OS shut down after the UPS has run on battery for 1 hour. Power to outlet group 1 will be cut 5 minutes after the OS shut down begins. Assuming the OS will power down in less than 5 minute the setting are good.  

BillP
Administrator Administrator
Administrator
0 Likes
0
276

Re: Are these setting s correct?

This reply was originally posted by Paul on APC forums on 7/23/2019


Thanks! Just wanted to be sure.

BillP
Administrator Administrator
Administrator
0 Likes
0
276

Re: Are these setting s correct?

This reply was originally posted by Paul on APC forums on 7/23/2019


What if I choose "Do not shut down when power fails" and then under "Operating system and application shutdown" I put 600 seconds? Will it run until there are 600 seconds left on battery and then shutdown the machine?

BillP
Administrator Administrator
Administrator
0 Likes
0
276

Re: Are these setting s correct?

This reply was originally posted by Bill on APC forums on 7/24/2019


On 7/23/2019 4:39 PM, Paul said:

What if I choose "Do not shut down when power fails" and then under "Operating system and application shutdown" I put 600 seconds? Will it run until there are 600 seconds left on battery and then shutdown the machine?

When a Power Outage occurs:
The shutdown process will not start until the remaining UPS runtime falls below the combined time configured for Application and Operating System shutdown. If you set the OS shutdown to 600 seconds when the runtime falls below 600 seconds a shutdown will be triggered.

 