Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82449members
349990posts

APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
gwitjes_apc
Ensign
Ensign
0 Likes
1
105

APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?

This was originally posted on APC forums on 5/20/2014


We have a Symmetra LX 16000 (SYA8K16PXR), with nine SYTB5 batteries (each less than a year old) in the XR1 rack, and three 4kVA power modules, but have the following Power Draw status (see image below).

Would we get better Runtime if the load was better distributed across the Phase L1 and Phase L2 ?

2363_APC.png

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
105

Re: APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?

This reply was originally posted by Angela on APC forums on 5/20/2014


I don't think you'll get better runtime but you'd be less likely to overload the UPS in the event of a Power Module Failure. General load balancing principles should apply here though - you want to have approximately equal load on phases throughout the facility.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
106

Re: APC Symmetra LX 16000 (SYA8K16PXR) - Phase L1 and L2 - spread load to increase Runtime?

This reply was originally posted by Angela on APC forums on 5/20/2014


I don't think you'll get better runtime but you'd be less likely to overload the UPS in the event of a Power Module Failure. General load balancing principles should apply here though - you want to have approximately equal load on phases throughout the facility.