Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82453members
350002posts

AP9617 Mass Programming NTP

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
sdmoore68_apc
Cadet
0 Likes
1
162

AP9617 Mass Programming NTP

This was originally posted on APC forums on 11/13/2011


I manage 1,400 different Smart-UPS 1500 RM, all have AP9617 NMCs in 7 different time zones. Using the INI Utility, I scripted all the NMCs to point to a primary and secondary NTP server, updates run every 168 hours. Here is my config.ini that is uploaded to all the east coast NMCs:

DateFormat=mm/dd/yyyy
DSTConfiguration=Traditional US
NTPEnable=enabled
NTPPrimaryServer=PrimaryIP
NTPSecondaryServer=SecondaryIP
NTPTimeZone=-05:00
NTPUpdateInterval=168

After the script ran, the NMCs did not contact the NTP server and consequently all times are not correct. Is there a way to force the UPS to contact the NTP server without logging into all 1,400 NMCs and clicking UPDATE NOW? Looking for something like script command like NTPUpdateNow=1.

Message was edited by: sdmoore68


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
162

Re: AP9617 Mass Programming NTP

This reply was originally posted by Angela on APC forums on 11/14/2011


someone asked me this recently and i think i discovered that there is not a way to do it unfortunately. if you're making other changes that force the card to reboot to take affect, that should do the trick. i understand this is not ideal though.

also, i havent tested it but disabling/enabling NTP should do it 😕

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
163

Re: AP9617 Mass Programming NTP

This reply was originally posted by Angela on APC forums on 11/14/2011


someone asked me this recently and i think i discovered that there is not a way to do it unfortunately. if you're making other changes that force the card to reboot to take affect, that should do the trick. i understand this is not ideal though.

also, i havent tested it but disabling/enabling NTP should do it 😕